#24089 - 01/18/14 12:58 PM Re: Ocelot doesn't work [Re: ADI Tech Support]
Auto control Offline
newbie


Registered: 01/16/14
Posts: 12
Hi Kevin
thanks for the reply and assist
correct will learn the IR from the Foxtel IQ2 remote so it will learn and at the same time function the devive while learning but will not send correct code from secondary HA device

Top
#24090 - 01/18/14 01:06 PM Re: Ocelot doesn't work [Re: Auto control]
Guy Lavoie Administrator Offline
Beyond All Hope
*****

Registered: 12/21/02
Posts: 6548
Loc: Montreal, QC, Canada
Have you tried specifying different carrier frequencies? Try learning the same code but enter a frequency of 56k instead of 32k, and see if that works.
_________________________
"If you don't know what you're doing, do it neatly..."

Top
#24091 - 01/18/14 04:35 PM Re: Ocelot doesn't work [Re: Guy Lavoie]
ADI Tech Support Moderator Offline
old hand


Registered: 12/22/02
Posts: 733
Loc: Branson West, MO
Once you learn the IR into the Ocelot, in C-Max go to Controller Utilities, debug timers and variables. Display variable 60 and point your remote to the IR window on the Ocelot and press the button you learned. Does variable 60 reflect the IR number you learned for that button?

If yes, then the ir command is properly learned into the Ocelot and it could just be a matter of placing the ir transmitter over the devices receiver better.

If not (variable 60 reports a value other than the IR number learned), go to http://www.remotecentral.com and find your devices IR codes. You may need to use IR Max to load these IR commands into the Ocelot. As Guy suggested, you will need to know the IR frequency for that device.

Kevin Barrett
ADI Tech Support

Top
#24092 - 01/19/14 12:47 PM Re: Ocelot doesn't work [Re: ADI Tech Support]
liutart Offline
newbie


Registered: 01/06/14
Posts: 19
Loc: Italy
I installed the new chips on Ocelots and one work properly, while the other one has problems. It has started butvwhen I attacched it to C-max it asked me for dowload executive and while it was updating has lost connnection. Now it doesn't work at all. Comms led blink one time when it is powered up and then nothing. IR led blinks if I send an IR with a remote control. But Active led is off and it doesn't connect with c-max.
Top
#24093 - 01/19/14 11:58 PM Re: Ocelot doesn't work [Re: liutart]
Auto control Offline
newbie


Registered: 01/16/14
Posts: 12
Hi Guy and Kevin
thanks for the help I will give that a Go
if any other ideas willing to give it a go
I will have to look at these before installing
can they be copied and paste separately
0 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 000A 0006 000A 0006 0CAF
1 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 000A 0006 0010 0006 0CA9
2 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0CA3
3 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 000A 0006 001C 0006 0C9D
4 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 0010 0006 000A 0006 0CA9
5 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 0010 0006 0010 0006 0CA3
6 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 0010 0006 0016 0006 0C9D
7 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 0010 0006 001C 0006 0C96
8 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 0016 0006 000A 0006 0CA3
9 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 0016 0006 0010 0006 0C9D
Active 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 001C 0006 001C 0006 001C 0006 0010 0006 0C72
AV 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 001C 0006 0016 0006 000A 0006 0C90
Back 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 0016 0006 0016 0006 0010 0006 0C90
Blue 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 001C 0006 000A 0006 000A 0006 0C96
Channel Down 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 0016 0006 000A 0006 0010 0006 0C9D
Channel Up 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 0016 0006 000A 0006 000A 0006 0CA3
Down 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0010 0006 0016 0006 0010 0006 0C90
Fast Forward 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 0016 0006 0016 0006 000A 0006 0C96
Foxtel 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0016 0006 000A 0006 001C 0006 0016 0006 0C84
Green 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0016 0006 001C 0006 0016 0006 0C7E
Guide 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 001C 0006 000A 0006 001C 0006 000A 0006 0C8A
Help 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 0010 0006 0C9D
Info 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 001C 0006 001C 0006 0C8A
Left 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0010 0006 0016 0006 0016 0006 0C8A
OK 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0010 0006 001C 0006 000A 0006 0C90
On Demand 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 001C 0006 0010 0006 0010 0006 0010 0006 0C8A
Pause 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 001C 0006 000A 0006 000A 0006 0C9D
Planner 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 001C 0006 001C 0006 0010 0006 000A 0006 0C84
Play 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 0016 0006 001C 0006 000A 0006 0C90
Power 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 000A 0006 001C 0006 000A 0006 0C9D
Record 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 001C 0006 0010 0006 001C 0006 0C84
Red 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0016 0006 001C 0006 0010 0006 0C84
Rewind 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 0016 0006 0016 0006 0010 0006 0C90
Right 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0010 0006 0016 0006 001C 0006 0C84
Set Up 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0010 0006 0010 0006 000A 0006 0C9D
Stop 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 000A 0006 001C 0006 000A 0006 0010 0006 0C96
Up 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0010 0006 0016 0006 000A 0006 0C96
Yellow 0000 0073 0000 0012 000F 000A 0006 000A 0006 0016 0006 000A 0006 0010 0006 0016 0006 0016 0006 000A 0006 000A 0006 000A 0006 0016 0006 0010 0006 0016 0006 0010 0006 0016 0006 001C 0006 001C 0006 0C78

Top
#24099 - 01/22/14 10:25 AM Re: Ocelot doesn't work [Re: ADI Tech Support]
liutart Offline
newbie


Registered: 01/06/14
Posts: 19
Loc: Italy
I installed the new chips on Ocelots and one work properly, while the other one has problems. It has started bat when I attacched it to C-max it asked me for dowload executive and while it was updating has lost connnection. Now it doesn't work at all. Comms led blink one time when it is powered up and then nothing. IR led blinks if I send an IR with a remote control. But Active led is off and it doesn't connect with c-max.
Top
#24100 - 01/22/14 10:45 AM Re: Ocelot doesn't work [Re: liutart]
ADI Tech Support Moderator Offline
old hand


Registered: 12/22/02
Posts: 733
Loc: Branson West, MO
Is one still working and the other not working?

Kevin Barrett
ADI Tech Support

Top
#24101 - 01/22/14 12:21 PM Re: Ocelot doesn't work [Re: ADI Tech Support]
liutart Offline
newbie


Registered: 01/06/14
Posts: 19
Loc: Italy
Yes, but as soon as I installed new Chips they was both working I think, but during updating executive something went wrong and now just one works.
Top
#24102 - 01/22/14 01:34 PM Re: Ocelot doesn't work [Re: liutart]
ADI Tech Support Moderator Offline
old hand


Registered: 12/22/02
Posts: 733
Loc: Branson West, MO
If you swap the chips between the two Ocelots, does the problem follow that chip?

Kevin Barrett
ADI Tech Support

Top
#24103 - 01/22/14 01:40 PM Re: Ocelot doesn't work [Re: ADI Tech Support]
liutart Offline
newbie


Registered: 01/06/14
Posts: 19
Loc: Italy
I can test it tomorrow and then I will tell you.
Thanks a lot for your support

Top
#24105 - 01/23/14 07:50 AM Re: Ocelot doesn't work [Re: liutart]
liutart Offline
newbie


Registered: 01/06/14
Posts: 19
Loc: Italy
I have just test them and the Ocelot works both properly with the same Chip.
Top
#24106 - 01/24/14 01:41 AM Re: Ocelot doesn't work [Re: liutart]
Auto control Offline
newbie


Registered: 01/16/14
Posts: 12
Still No Luck with this Foxtel IQ2 and Ocelot
the system dose not work unless
I point the remote control at the ocelot then and only then does it work
if I learn it in No LUCK
I checked variable 60 and it was OK code number 4
IR code number that was learnt in
TRANSMISSION FAILURE oh it does not give any error code just does not work
any help would be fine
?? the IR remote can work as said but only at a distance of 400 mm or more I think the signal is toooo strong

Top
#24107 - 01/24/14 04:10 AM Re: Ocelot doesn't work [Re: Auto control]
Guy Lavoie Administrator Offline
Beyond All Hope
*****

Registered: 12/21/02
Posts: 6548
Loc: Montreal, QC, Canada
Have you tried the different carrier frequency?
_________________________
"If you don't know what you're doing, do it neatly..."

Top
#24108 - 01/24/14 01:12 PM Re: Ocelot doesn't work [Re: Guy Lavoie]
liutart Offline
newbie


Registered: 01/06/14
Posts: 19
Loc: Italy
I have just test them and the Ocelot works both properly with the same Chip.
Top
#24109 - 01/24/14 01:46 PM Re: Ocelot doesn't work [Re: liutart]
ADI Tech Support Moderator Offline
old hand


Registered: 12/22/02
Posts: 733
Loc: Branson West, MO
Looks like the chip got corrupted on the download. E-Mail me (kevinbarrett@appdig.com) and I'll get you another one out.

Kevin Barrett
ADI Tech Support

Top
#24110 - 01/24/14 02:24 PM Re: Ocelot doesn't work [Re: ADI Tech Support]
Auto control Offline
newbie


Registered: 01/16/14
Posts: 12
Hi Guy
Yes but not all carrier frequencies from 30K to 150K
all 30K ranges half of the 50K range
half of the 70K range and then 120, 130, 150
some where around multiples of 38K
No Luck

Top
#24121 - 01/29/14 03:04 PM Re: Ocelot doesn't work [Re: Auto control]
Auto control Offline
newbie


Registered: 01/16/14
Posts: 12
Help my Foxtel does not respond
get R2D2 to give a hand any ideas

Top
#24122 - 01/29/14 06:40 PM Re: Ocelot doesn't work [Re: Auto control]
Guy Lavoie Administrator Offline
Beyond All Hope
*****

Registered: 12/21/02
Posts: 6548
Loc: Montreal, QC, Canada
What is the name and model number of this Foxtel device?
_________________________
"If you don't know what you're doing, do it neatly..."

Top
#24123 - 01/29/14 07:24 PM Re: Ocelot doesn't work [Re: Guy Lavoie]
ADI Tech Support Moderator Offline
old hand


Registered: 12/22/02
Posts: 733
Loc: Branson West, MO
Did you try loading the IR codes into IR-Max and see what they look like?

Kevin Barrett
ADI Tech Support

Top
#24124 - 02/03/14 04:34 PM Re: Ocelot doesn't work [Re: ADI Tech Support]
Auto control Offline
newbie


Registered: 01/16/14
Posts: 12
OK so the Foxtel unit is a
Pace TD480NF
as I have said earlier the unit responds to IR if the IR is directed at the Oce3lot IR learing IR detector
but will not respond if sent from Ocelot or Hal2000
is this ocelot capable of sending GHz to IR or only MHz
and what about the Xantech IR extender 789-44
any idears

Thanks Geoff

Top
Page 2 of 3 <123>


Moderator:  Dan Smith, Monte G, ADI Tech Support, Guy Lavoie 
Hop to:
Who's Online
0 registered and 22 anonymous users online.
Recent Posts
Shout Box

Newest Members
brigiel, vevevie, zhutree, 416, saiqul
3003 Registered Users
Forum Stats
3003 Members
19 Forums
4006 Topics
23465 Posts

Max Online: 132 @ 11/13/16 10:07 AM
June
Su M Tu W Th F Sa
1 2
3 4 5 6 7 8 9
10 11 12 13 14 15 16
17 18 19 20 21 22 23
24 25 26 27 28 29 30