Chris,
First you set up the AT 200s with the AT100 using the AUTOMATIONtec web page.
The AT Series connects to the Ocelot via the COM A and B connections on the AT100. When addressing the system, you need to reserve 30 addresses for the AT (That's how many modules the AT100 can control). As a matter of practice, it's a good idea to have the AT modules address be after the last address you have a regular ADICON2500 module set to.
Auto address you modules as before. You will press the white address button on the AT100 to address the AT100.
The next 30 address will be reserved for the AT200s. So for example, if you have 10 regular ADICON2500 modules addressed 1-10,and you address the AT100 as module 11, the AT200 modules will take addresses 11-40. The AT200 showing at address 1 on the AUTOMATIONtec 100 page will be module 11 in C-Max, in this example, and so on.
In C-Max, you will use the Bobcat modules as your modules for the If-Then-Else programming. So if your ATEC module is a tempurature module, you will call it a Bobcat temp module in the C-Max system map. You will treat it as a Bobcat in your If-Then-Else programming.
Kevin Barrett ADI Tech Support
|