#21818 - 04/26/10 02:26 PM Think I burned up my SECU16...
Don Stephens Offline
newbie


Registered: 08/17/04
Posts: 16
Loc: Hamilton, MT
I have been trying to use a SECU16 as a controller for my sprinklers, and in the process, I probably burned up my SECU16.

I am using a 24VT transformer from my furnace to control 5 electric valves. The longest run worked for a day or so and now will not turn off. There is continuity between the relay connectors even though the software tells me that that relay is open. I'm assuming that there is too much current for the relay.
Is this correct?

Thanks;

Don


Edited by Don Stephens (04/26/10 02:28 PM)

Top
#21819 - 04/26/10 05:26 PM Re: Think I burned up my SECU16... [Re: Don Stephens]
Guy Lavoie Administrator Offline
Beyond All Hope
*****

Registered: 12/21/02
Posts: 6401
Loc: Montreal, QC, Canada
That is probably the problem. Do a search on the forum for "sprinkler" and you will find several discussions about this. The problem is with the current spike that the sprinkler's solenoid coil induces in the relay's contacts when the solenoid is turned off. You might be able to get the relay to unstick by snapping it with your fingers a few times. If that works, then look into using small external relays to avoid damaging the SECU16 relays.
_________________________
"If you don't know what you're doing, do it neatly..."

Top
#21820 - 04/27/10 06:52 AM Re: Think I burned up my SECU16... [Re: Guy Lavoie]
ADI Tech Support Moderator Offline
addict


Registered: 12/22/02
Posts: 608
Loc: Branson West, MO
Don,

I would recommend using a RLY8XA for this application. The relays on it will be able to handle the load.

Kevin Barrett
ADI Tech Support

Top
#21821 - 04/27/10 07:12 AM Re: Think I burned up my SECU16... [Re: ADI Tech Support]
John Vomastic Online   content
active contributor


Registered: 01/26/03
Posts: 135
Loc: Manitou Springs, Colorado
I have had similar problems trying to use the SECU16 relays for other than really small loads. I now use Elk relays (Elk-912) with the SECU16 for a number of applications around the house. Never had a problems.

http://www.elkproducts.com/support/training/t1_relays.htm

Top
Page 1 of 1 1


Moderator:  Dan Smith, Monte G, ADI Tech Support, Guy Lavoie 
Hop to:
Who's Online
0 registered and 26 anonymous users online.
Recent Posts
how to post an icon
by manu
02/03/12 03:40 AM
Command Pair
by kuro
02/01/12 12:49 AM
Does anyone have a copy of the latest TSE?
by sevenzenith1
01/30/12 05:17 AM
Have HAL2000 do the work or the Ocelot?
by khem
01/28/12 02:49 PM
Ocelot + Powermid = Fail
by Guy Lavoie
01/27/12 03:37 PM
Shout Box

Newest Members
dfgg, manu, kuro, sevenzenith1, chuck214
2748 Registered Users
Forum Stats
2747 Members
19 Forums
3835 Topics
22711 Posts

Max Online: 67 @ 08/16/11 03:08 PM
February
Su M Tu W Th F Sa
1 2 3 4
5 6 7 8 9 10 11
12 13 14 15 16 17 18
19 20 21 22 23 24 25
26 27 28 29