Hi

I was wondering if you guys can help me with this

Setup
1. 4 magnetic switches Door 1,2,3,4
2. all 4 switches are connected to 4 SECU16 inputs 0,1,2,3
3. All 4 inputs interconnected with SECU 16 Relay output 7
4. Relay 7 controls additional Relay which controls 2 LED’s Red and Green – Go Home Light

Everything work except the “end sequence”
I now where the mistake is but I don’t know how to fix it

If Door A is opened - Red LED ON
If Door A is closed – Green LED ON

Problem

If the Door A is opened – Red LED ON
And the Door B is opened Red LED ON
Than Door A is closed – Green LED ON
Door B is still opened

I want to have a Green light only if all doors are closed

0271 - IF Module #5 -SECU16 Input #0 Turns OFF //
0272 - THEN Transmit X10, K - 1 //
0273 - THEN Transmit X10, K - ON (19) //
0274 - THEN Module #5 -SECU16 Relay #14 Turn ON //
0275 - IF Module #5 -SECU16 Input #0 Turns ON //
0276 - THEN Module #5 -SECU16 Relay #14 Turn OFF //
0277 - //
0278 - IF Module #5 -SECU16 Input #1 Turns OFF //
0279 - THEN Transmit X10, K - 1 //
0280 - THEN Transmit X10, K - ON (19) //
0281 - THEN Module #5 -SECU16 Relay #14 Turn ON //
0282 - IF Module #5 -SECU16 Input #1 Turns ON //
0283 - THEN Module #5 -SECU16 Relay #14 Turn OFF //
0284 - //
0285 - IF Module #5 -SECU16 Input #2 Turns OFF //
0286 - THEN Transmit X10, K - 1 //
0287 - THEN Transmit X10, K - ON (19) //
0288 - THEN Module #5 -SECU16 Relay #14 Turn ON //
0289 - IF Module #5 -SECU16 Input #2 Turns ON //
0290 - THEN Module #5 -SECU16 Relay #14 Turn OFF //
0291 - //
0292 - IF Module #5 -SECU16 Input #3 Turns OFF //
0293 - THEN Module #5 -SECU16 Relay #14 Turn ON //
0294 - IF Module #5 -SECU16 Input #3 Turns ON //
0295 - THEN Module #5 -SECU16 Relay #14 Turn OFF //
0296 - // XXXXXXXXXXXXXXXXXXXX
0297 - IF Touch Object #107, Button Leopard is pressed // GARAGE OPENED/CLOSED
0298 - AND Module #5 -SECU16 Input #3 Is ON // MAGNETIC CONTACT SWITCH
0299 - THEN Module #5 -SECU16 Relay #15 Turn ON // RELAY 8 GARAGE OPENER
0300 - THEN Timer #1 = 1 //
0301 - IF Timer #1 becomes > 3 //
0302 - THEN Module #5 -SECU16 Relay #15 Turn OFF //
0303 - THEN Timer #1 = 1 //
0304 - IF Module #5 -SECU16 Input #3 Is OFF //
0305 - THEN Variable #41 = 0 // GARAGE OPENED
0306 - THEN Touch Object #107 displays Icon# Garage opened.bmp //
0307 - IF Variable #41 becomes = 0 //
0308 - AND Module #5 -SECU16 Input #3 Turns OFF //
0309 - THEN Send Module #7 -SPEAK-EZ Audio Message #1 //
0310 - //
0311 - IF Touch Object #107, Button Leopard is pressed // GARAGE OPENED/CLOSED
0312 - AND Module #5 -SECU16 Input #3 Is OFF // MAGNETIC CONTACT SWITCH
0313 - THEN Module #5 -SECU16 Relay #15 Turn ON // RELAY 8 GARAGE OPENER
0314 - THEN Timer #2 = 1 //
0315 - IF Timer #2 becomes > 3 //
0316 - THEN Module #5 -SECU16 Relay #15 Turn OFF //
0317 - THEN Timer #2 = 1 //
0318 - IF Module #5 -SECU16 Input #3 Is ON //
0319 - THEN Variable #41 = 1 // GARAGE CLOSED
0320 - THEN Touch Object #107 displays Icon# Garage closed.bmp //
0321 - IF Variable #41 becomes = 1 //
0322 - AND Module #5 -SECU16 Input #3 Turns ON //
0323 - THEN Send Module #7 -SPEAK-EZ Audio Message #2 //



1021

Top
#17117 - 01/11/07 01:34 PM Re: Go Home Light [Re: 1021]
Guy Lavoie Administrator Offline
Beyond All Hope
*****

Registered: 12/21/02
Posts: 6548
Loc: Montreal, QC, Canada

The problem is that you're looking for a dynamic triggering condition (Turns ON) for 4 different inputs to control relay #14. This doesn't work because another input might have changed in the meantime. The best way to do this is with a flag, by testing all 4 inputs statically, with any one of them setting the flag. Finally if the flag is set, then activate the relay. By looking for the flag to "become" a new value, you only set the relay when the flag actually changes.

It is not clear from your code if an open door turns an input on or off so in this example I'm assuming an open door turns on an output. If its the opposite, then change lines 283 to 286 to "Is OFF". Same thing with the red/green LED. I'm assuming that the relay being turned on shows a red LED. If its the opposite then change lines 291 and 293 accordingly. In this example I'm using variable #99 as the flag:


0271 - IF Module #5 -SECU16 Input #0 Turns OFF //
0272 - THEN Transmit X10, K - 1 //
0273 - THEN Transmit X10, K - ON (19) //
0274- //
0275 - IF Module #5 -SECU16 Input #1 Turns OFF //
0276 - THEN Transmit X10, K - 1 //
0277 - THEN Transmit X10, K - ON (19) //
0278 - //
0279 - IF Module #5 -SECU16 Input #2 Turns OFF //
0280 - THEN Transmit X10, K - 1 //
0281 - THEN Transmit X10, K - ON (19) //
0282 - //
0283 - IF Module #5 -SECU16 Input #0 Is ON // if any door is open
0284 - OR Module #5 -SECU16 Input #1 Is ON //
0285 - OR Module #5 -SECU16 Input #2 Is ON //
0286 - OR Module #5 -SECU16 Input #3 Is ON //
0287 - THEN Variable #99 = 1 //then set flag
0288 - ELSE Variable #99 = 0 //else clear flag
0289 - //
0290 - IF Variable #99 becomes = 1 //if flag just got set
0291 - THEN Module #5 -SECU16 Relay #14 Turn ON // then show red LED
0292 - IF Variable #99 becomes = 0 //if flag just got cleared
0293 - THEN Module #5 -SECU16 Relay #14 Turn OFF // then show green LED

0296 - // XXXXXXXXXXXXXXXXXXXX
...



Note that since the first 3 inputs turning off have the same action (turning K1 on) you could furthur reduce lines 271 to 281 to:


0271 - IF Module #5 -SECU16 Input #0 Turns OFF //
0272 - OR Module #5 -SECU16 Input #1 Turns OFF //
0273 - OR Module #5 -SECU16 Input #2 Turns OFF //
0274 - THEN X10, K - 1 Turn ON // use X10 quick on/off instruction
_________________________
"If you don't know what you're doing, do it neatly..."

Top
#17118 - 01/11/07 07:05 PM Re: Go Home Light [Re: 1021]
1021 Offline
junior
*

Registered: 09/12/06
Posts: 34
Loc: Mississauga, Ontario, Canada
it works...of course
believe it or not I had similar idea with a variable set up as a flag but I got lost between "or" and "else" command. It looks like I have a long way to go. Obviously I am new at this.

Many thanks for your help.

I hope you will be around for a while...

1021

Top
#17119 - 01/11/07 09:15 PM Re: Go Home Light [Re: 1021]
Guy Lavoie Administrator Offline
Beyond All Hope
*****

Registered: 12/21/02
Posts: 6548
Loc: Montreal, QC, Canada
_________________________
"If you don't know what you're doing, do it neatly..."

Top
Page 1 of 1 1


Moderator:  Dan Smith, Monte G, ADI Tech Support, Guy Lavoie 
Hop to:
Who's Online
0 registered and 49 anonymous users online.
Recent Posts
Shout Box

Newest Members
brigiel, vevevie, zhutree, 416, saiqul
3003 Registered Users
Forum Stats
3003 Members
19 Forums
4000 Topics
23426 Posts

Max Online: 132 @ 11/13/16 10:07 AM
August
Su M Tu W Th F Sa
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29 30 31